Télécharger Imprimer la page

Publicité

Les langues disponibles

Les langues disponibles

Built in

Electrical connection
For the connection, use an approved cable,
in accordance with the regulations. The
cable casing should be of rubber..
There is a label on the underside of the
appliance with the wiring diagrams. The
connection terminals are accessible once
you have opened the junction box on the
underneath. The junction box cover can be
opened with a screwdriver.
If you want to make a fixed connection,
make sure that a multi-polar switch with a
contact separation of at least 3 mm is fitted
in the supply line.
Power setting table
Type of hob
T265
A266
Highlight
x
x
Electrical connection
230 V - 50 Hz
x
x
Power of elements
Front left
2300 W
Front left double
2200/1000 W
Rear left
1200 W
1200 W
Rear right
2000 W
2000 W
Front right
1200 W
1200 W
The appliance can be connected in the
following ways:
1 phase connection (1 1N a.c. 230 V / 50 Hz):
The voltage between live and neutral is
i230 V a.c. Install connecting bridges between
connection points 1-2 and 4-5.
Your group must be protected by a fuse of at
least 32 A. The connecting power cable must
have a minimum core cross section of 6 mm
2 lives with 2 neutrals connection
(2 2N a.c. 230 V / 50 Hz):
The voltage between live and neutral is 230 V
a.c. There may be a voltage of 0 V between
the phases if they are connected to the same
phase in the meter cupboard but also 400 V if
they are connected to 2 different phases. Your
groups must be fused with at least 16 A (2x).
The connecting power cable must have a
minimum core cross section of 2,5 mm2.
2
.
2 lives with 1 neutral connection
(2 1N a.c. 400 V / 50 Hz):
The voltage between the phases and the
neutral is 230 V a.c. Between the lives there is
a voltage of 400 V. If there is not a voltage of
400 V between the lives, two wires have been
taken from the same live in the meter
cupboard and the hob must be connected
with two neutral wires, as indicated above
under 2 lives with 2 neutrals. Install a
connecting bridge between the connection
points 4-5.
Your groups must be fused with at least 16 A
(2x). The connecting power cable must have a
minimum core cross section of 2,5 mm
2
.
3 lives with 1 neutral connection
(3 1N a.c. 400 V / 50 Hz):
The voltage between the phases and the
neutral is 230 V a.c. There is a voltage of 400 V
between the lives. Fit a connecting bridge
between the connection points 4-5. Phase 3
carries no load. Your groups must be fused
with at least 16 A (3x). The connecting power
cable must have a minimum core cross
section of 2,5 mm
2
.

Publicité

loading

Ce manuel est également adapté pour:

A266